bradleydavidgood777, to better understand the connector wiring, google "nema wiring chart" which will show you the myriad of ways every connector should be wired.
Three-wire 240vac circuits utilize HOT-HOT-GROUND.
The reason the US code was changed to require four-wire instead of three-wire 240vac circuits is that many 240vac appliances started using 120vac (one leg of the input) for their control circuitry, which resulted in current flow in the ground wire. With the change, 120vac current flow is now properly routed through the Neutral wire back to the service panel, maintaining the sefety integrity of the separate ground wire.
As we said earlier, 240vac EVSEs normally only use the two hot wires, with a safety ground. Some confusion was interjected into this discussion regarding the Amazing-E and its internal configuration. I am not surprised that the Neutral connection is unused on the Amazing-E. As was pointed out, cutting off the Neutral pin will allow this connector to plug into either a 14-30 or 14-50 outlet, and you can make a simple adapter to plug it into your old-style 10-30 dryer outlet.
Bottom line, it appears that all you need to bring out is three wires: Hot-Hot-Ground
Don said:
Is that outlet on it's own breaker?? - If so, you have a really, really easy solution to your L2 charging problems